Re: emi
Posted: 02 Jul 2022, 00:26
If your neutral to ground is always giving you 0 potential that means they are bonded, probably at the main panel of your house or the main panel of your building. It's common practice to do so specially when your energy company also supplies the ground line. Make sure it's not bonded somewhere in between "sub panels for example", since that will cause a ground loop and it is also against general regulations. If your ground is bonded to the neutral at your socket, then please call an electrician lol.MegaMelmek wrote: ↑01 Jul 2022, 14:58Hot - Neutral 240-247V +-Xehet wrote: ↑30 Jun 2022, 11:38You need a Multimeter (also known as AVOmeter) to check your grounding quality and stability. It can be a simple model, you don't need to buy an expensive one. After you get a multimeter what you want to do is to take certain measurements on the outlet you use for your pc, you can also test your extension cord afterwards as well;MegaMelmek wrote: ↑30 Jun 2022, 10:25I am not sure what values you mean so if you can specifi them ?
First: Check if your voltage is stable by inserting one of your probes to hot and other one to neutral. If the value is around your country standard ±5% it is stable, the value should not be jumpy, if it is jumpy your probes are not still/you are moving your probes around.
Second: Leave the first probe in hot and move the second probe which was in neutral to grounding and check if your readings are the same as the first step, they should be roughly the same.
Third: Move the first probe from hot to neutral and leave the second probe in ground and please share your values for all the steps, especially the third step with your country standard voltage.
P.S. While using a multimeter make sure that the multimeter is set to a higher value than your country standard, e.g. your country has a standard of 230 volts, then make sure that your multimeter is set to a higher value and not 200 etc. you can set to lower values for a more precise reading for the third step after you make sure that you first read the value while keeping the multimeter on a higher setting, in case your grounding is connected to neutral, which should not be the case but some houses have such issues. If you drop the multimeter reading setting to below the voltage it receives you will blow your fuse/damage the multimeter.
Hot- Ground - same values as above
Neutral - Ground - 0V never change
Multimeter : UNI-T UT181A
In a good case scenario, a ground to neutral potential can be anywhere between 0.1 - 2.0 volts. FYI, I was having the input lag and desync issues way before I ever installed grounding in my home. Upon installing it, the PC ran fantastic for about 5 days then shit started coming back, maybe that's what you're experiencing? anytime a change happens to reference ground things get reset back to normal? who knows.